Hello, While running a heatpump simulation I get below error Invalid value for ttd_u: ttd_u = -1.6613626246231092 below minimum value (0) at component condenser. On checking my temperature values for refrigerant and water In my knowledge ttd_u is hot_in temperature - cold_out temperature If can someone help. Thanks, |
Beta Was this translation helpful? Give feedback.
Replies: 2 comments 2 replies
-
|
Hi @ronitd07, the definition of the Best |
Beta Was this translation helpful? Give feedback.
-
|
Hi @fwitte Thanks for your help and clarification. But I also need to use subcooling at the end of my condensor which I was using with Condensor component but subcooling is not available with MovingBoundaryHeatExchanger I guess as i get an error that it has no attribute subcooling. Thanks, |
Beta Was this translation helpful? Give feedback.
Hi @ronitd07,
the definition of the
Condensercomponent is a bit different in that context. The component comes from steam power plants, where the upper terminal temperature usually indicates temperature difference between condensing temperature and cold side temperature exit, disregarding potential desuperheating. I recommend you use the MovingBoundaryHeatExchanger instead, also see the tutorials on the heat exchangers here: https://tespy.readthedocs.io/en/main/advanced_tutorials/heat_exchangers.html#tutorial-heat-exchanger. This shows the differences between the different classes.Best