Calculation of td_log in heat exchangers with constant temperature difference #394
Closed
dk-teknologisk-enp
started this conversation in
Ideas
Replies: 2 comments
-
|
Dear @dk-teknologisk-enp, that sounds like a very good idea. It seems I have never come across this bug in 6 years of development and using the software. Thanks a lot. Do you like to make the changes in a pull request yourself? I‘ll be in holidays one more week and can only implement the changes once I get back to work. best Francesco |
Beta Was this translation helpful? Give feedback.
0 replies
-
|
Hi Francesco, I have made this PR: #396 I have not added any tests, but that might be a good idea. |
Beta Was this translation helpful? Give feedback.
0 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
-
Currently it seems that if ttd_u == ttd_l for a heat exchanger, then td_log ends up as nan, and thus also the kA.
However, this is a perfectly valid situation, for example in a heat exchanger with purely boiling/condensing on both sides.
I suggest making the following changes to base.py, such that td_log is set to the constant temperature difference in case ttd_u == ttd_l:
(base.py:838-840)
Beta Was this translation helpful? Give feedback.